Gas pipes in a communal area

Home Forums ASCP Forum Gas pipes in a communal area

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #10008
    Neil Tuck
    Participant

    Need calcification on what can or can’t be run in a communal area if you can’t use soldered joints, can you use compression fitting? is the whole of the communal area with communal door still classed as protected area?

    #10016
    Trevor Percy
    Participant

    Hi Neil,

    There was a good presentation at one of last years AGSM Technical meetings that covered this and it’s on the AGSM portal to download.

    http://www.agsm.uk.com/wp-content/uploads/2017/11/CORGI-AGSM-Gas-in-Multi-Occupancy-Buildings-1.pdf

    #11177
    Darren Mould
    Participant

    This is my understanding in accordance with BS6891, and if anyone has anything to add then please feel free. If the pipework is exposed in the protected area, ie not inside it’s own purpose made duct, then there are a couple of options, but compression fittings cannot be used in any circumstance.
    1. If there is ventilation at both high and low level direct to outside air in the protected area then BS6891 clause 8.19.1 states that the following can be used:
    a) steel pipework with screwed joints;
    b) steel pipework with welded joints;
    c) continuous length of copper (no joints) or;
    d) continuous length of pliable corrugated (stainless-steel) tubing manufactured to withstand fire test A of BS EN 1775:2007, Annex A.

    2. If there is no ventilation at high and low level in the protected area then the pipework can still be exposed to, and run through the protected area in accordance with clause 8.19.4, whereby the pipe work must be continuous or welded and meet the requirements of 8.19.1b), c) or d), provided that the protected area is normally occupied. This means normally used common lobbies or corridors that have regular passers through.

    There are some different requirements where the pipe runs through suspended ceilings and if it is run in its own purpose built duct.